Afrikaans Arabic Belarusian Bulgarian Catalan Czechoslovakia Cyprus Germany  Spanish  Ethiopia Persian Finnish French Irish Galician Hindi Croatian Hungarian Icelandic Italian Hebrew Japanese Korean Italian Latvian, Lettish Macedonian Malay Maltese Dutch Norwegian Polish Portuguese Romanian Russian Slovak Slovenian Albanian Serbian Swedish Swahili Thai Tagalog Turkish Ukrainian Vietnamese English
FreeWeldingForum.com Welding Forum Community presented by LONGEVITY  
+ Reply to Thread Share
Results 1 to 8 of 8

Thread: What gauge wire

  1. #1
    gilly's Avatar
    gilly is offline Senior Member
    Join Date
    Jul 2010
    Location
    Perdido Bch. Al.
    Posts
    763
    Images
    61
    Thanks
    0
    Thanked 21 Times in 21 Posts

    What gauge wire

    I am trying to run wire from my main power box to a sub box in my garage.The distance of wire including extra for hooking it up is 100ft.All the wire gauge calculators say #6 wire,but a welding company I use and some others I have talked to say #2 to be sure its big enough to carry the amperage 100ft.Would #6 be good enough,or should I use thicker?This stuff costs a bundle the bigger the wire gets,and I know they are trying to make as much money as they can off of the wire and I don't blame them,but I am retired and live on a fixed income,at least till I get my welder hooked up.Any suggestions from the pro's that know if #6 is plenty big enough.Thanks guys.
    Oh,I forgot to add it's for running 100 amps to the sub box.
    Last edited by gilly; 01-31-2011 at 10:45 AM.
    Guy

    Miller Syncrowave 250 DX
    Millermatic Challenger Mig
    Century 230/140 amp AC/DC Stick
    DeVilbiss 6Hp 60Gal.
    HF Horizontal/Vertical Bandsaw
    HF 6in. Belt 9in. Disc Sander
    HF pipe bender
    HF tubing roller

  2. #2
    Gadget's Avatar
    Gadget is offline Moderator
    Join Date
    Nov 2007
    Location
    Michigan
    Posts
    4,568
    Images
    138
    Thanks
    72
    Thanked 123 Times in 114 Posts
    You have to consider the amperage more than the voltage for the run. There are online wire gauge calculators you can use to determine what size you need but you have to know what amperage you are going to feed to the substation. Here is a link to a wire size calculator that factors in voltage, current, distance, and wire type. Wire Size Calculator
    Units owned
    Longevity WeldPro LS200PI (IGBT)
    Force Cut LP80 plasma cutter
    Longevity auto dark welding helmet

    Atlas 10x36" lathe
    Craftsman 5HP 30 Gal compressor
    Home made CNC router/plasma/hot wire foam cutting table powered by Longevity Force Cut LP80
    Home built aluminum foundry, HF 4x6 bandsaw, O/A torch

  3. #3
    gilly's Avatar
    gilly is offline Senior Member
    Join Date
    Jul 2010
    Location
    Perdido Bch. Al.
    Posts
    763
    Images
    61
    Thanks
    0
    Thanked 21 Times in 21 Posts
    Thanks Gadget, I edited it to say amperage.I used that chart you posted already and it said #6.I was wondering if that is the bare minimum wire size,or plenty good enough.I need 240 volts and 100 amps at the sub box,and was just looking for conformation that the chart was dead on,or just for reference.
    Guy

    Miller Syncrowave 250 DX
    Millermatic Challenger Mig
    Century 230/140 amp AC/DC Stick
    DeVilbiss 6Hp 60Gal.
    HF Horizontal/Vertical Bandsaw
    HF 6in. Belt 9in. Disc Sander
    HF pipe bender
    HF tubing roller

  4. #4
    odleo's Avatar
    odleo is offline Senior Member
    Join Date
    Feb 2008
    Location
    Ward, Arkansas
    Posts
    236
    Images
    15
    Thanks
    6
    Thanked 1 Time in 1 Post
    Gilly-- I had a sub panel installed in my garage and the electricain said I would need at least a #4 wire for the run which is about 110 foot from main panel. I had a 100 amp serivce installed. Not sure if it was required by code where I live or the electrcian was trying to make more money off me.
    Speedway 110 Flux core welder
    HF 80 amp arc welder
    Lincoln tombstone
    Really old and I mean old welder
    Lots of clamps, grinders
    And a desire to lean all I can about welding and fabrication
    Oh forgot I have gotten to use an awsome Longevity multi purpose machine and sweet enigne drive thanks to SIC Fabrications

  5. #5
    gilly's Avatar
    gilly is offline Senior Member
    Join Date
    Jul 2010
    Location
    Perdido Bch. Al.
    Posts
    763
    Images
    61
    Thanks
    0
    Thanked 21 Times in 21 Posts
    Yea odleo,I think I will go with the #4 wire also to be on the safe side.Thanks for the info.
    Guy

    Miller Syncrowave 250 DX
    Millermatic Challenger Mig
    Century 230/140 amp AC/DC Stick
    DeVilbiss 6Hp 60Gal.
    HF Horizontal/Vertical Bandsaw
    HF 6in. Belt 9in. Disc Sander
    HF pipe bender
    HF tubing roller

  6. #6
    odleo's Avatar
    odleo is offline Senior Member
    Join Date
    Feb 2008
    Location
    Ward, Arkansas
    Posts
    236
    Images
    15
    Thanks
    6
    Thanked 1 Time in 1 Post
    Glad was able to help.
    Speedway 110 Flux core welder
    HF 80 amp arc welder
    Lincoln tombstone
    Really old and I mean old welder
    Lots of clamps, grinders
    And a desire to lean all I can about welding and fabrication
    Oh forgot I have gotten to use an awsome Longevity multi purpose machine and sweet enigne drive thanks to SIC Fabrications

  7. #7
    KHK's Avatar
    KHK
    KHK is offline Moderator
    Join Date
    Oct 2008
    Location
    Chicago suburbs
    Posts
    2,559
    Images
    88
    Thanks
    0
    Thanked 52 Times in 50 Posts
    100 feet 100 amps calls for #4 wire
    keith
    The older the Boys, the more expensive the TOYS
    Previously Owned equipment;
    lot's
    Current equipment;
    3HP Speedair air compressor, Wilton drill press, Craftsman 10x36 lathe, 10 ton hydrolic press, Portaband band saw, OA torch, Small home brew CNC machine, powered by my 200PI
    2 Longevity autodarking helmets
    160d MIG
    WeldAll 200PI

  8. #8
    gilly's Avatar
    gilly is offline Senior Member
    Join Date
    Jul 2010
    Location
    Perdido Bch. Al.
    Posts
    763
    Images
    61
    Thanks
    0
    Thanked 21 Times in 21 Posts
    Thanks my friends,I appreciate it.I wanted to get this right the first time.I should have run a 200 amp service to my garage to start with,and I wouldn't have had to do this again.Oh well,live and learn.
    Guy

    Miller Syncrowave 250 DX
    Millermatic Challenger Mig
    Century 230/140 amp AC/DC Stick
    DeVilbiss 6Hp 60Gal.
    HF Horizontal/Vertical Bandsaw
    HF 6in. Belt 9in. Disc Sander
    HF pipe bender
    HF tubing roller