I have a whole house generator (Genrac 15KW) The generator supplyes 240vac three wire. From either hot leg to the other hot leg is 240vac. From either hot leg to neutral is 120vac. So I always have both 240vac and 120vac. This is normal home wireing. I think the problem is in the total amp draw.
GENERATOR SPECS:
Frequency : 60Hz
Max. AC Output: 6.5KW at 60Hz
Rated AC Out put: 5.7KW at 60Hz
Rated AC Voltage (V) :110,120, 220, 230, 110/220,120/240
200P Specifications:
Operating Voltage:
208/220vac 50/60HZ Input Single Phase 1PH
50amp cut draws 22.7A at 5KVA
40amp cut draws 17.6A at 3.8KVA
A plasma cut at 50 amp will draw 5 kva leaving only .7kw for the compressor. That is 700 watts which is about 1Hp. If you decrease the plasma cutter to 40 amp the picture is better 3.8kva for the cutter leaving 1.9kva for the compressor which is about 2.5 Hp. The peak generator power is 6.5kw the extra 1kw should allow the proper starting of the compressor. You may want to look into a soft start package for the compressor.
keith